Hi,
the issue is that the solar controller and the Setec have both been designed to be the MASTER controller. In my opinion, it makes much more sense to keep the Setec as the master controller. You then get a multi-stage 240V battery charger, a 240V to 12V power supply, ability to charge via the AUX input from the tug alternator, fuse distribution system, low voltage disconnect, and on the Setec III, the ability to completely isolate the battery from all loads.
You then add a roof mounted solar panel/controller to the system by connecting the battery terminals of the solar controller directly to the battery via an inline fuse. Keep the wiring from the controller to the battery as short as possible. You do not connect anything to the load terminals of the solar controller. In this way the solar controller is NOT the master controller and becomes the SECONDARY controller.
In more sophisticated controllers, you will be able to measure battery voltage, instantaneous current coming from the panels to the battery, and accumulated charge and possibly many other things.
Battery state of charge can (SOC) only be measured with no load on the battery, and some time after any charge has been put into the battery. I have found the best time to measure SOC when off grid is first thing in the morning. If you have a Setec III, then also switch the battery off to ensure there really is no load. You will need to print off a table or chart for your particular battery type which shows no load voltage against % SOC. AGM, GELs, and normal Lead Acid batteries differ in this regard.
Taking the SOC of the battery, you can then determine how many Ah must be generated during the day to fully restore the SOC to 100%. You need to add a bit more for efficiency losses (i.e the battery dissipates heat when it is charged and discharged). I would suggest adding about 10%. With time you will generally get a feel for how much power you are consuming per day.
After this you can get more complex by adding portable solar panels, a DC-DC charger to get higher charge rates to the van battery from the tug.
If contemplating putting charge into the van battery from a portable generator, I would strongly suggest not using the Setec but getting a more heavy duty multi-stage charger that will deliver more current. The reason is to charge the batteries faster, use less fuel, and annoy fellow yor campers much less.
As an example, assume a 100Ah battery and a Setec ST20 has a MAX charge rate of 10A. So, the maximum power going into the battery from the generator will be approximately 140W. (14V x 10A). Drwaing only 140W is tot really an efficient use of a 2kW generator! At 10A and a battery that is down to 50%SOC, it will take way longer than 5 hours to pump the 50Ah needed to fully charge a 100Ah battery. The reason it will be way longer is that the last part of the charging cycle to get the battery back to 100% will be done in float mode which will be charging at currents much less than 10A.
Now, a Ritar 100Ah battery has a maximum charging current of 20A. So, getting a good 20A multi-stage charger will pump twice as much into the battery from the generator. It will charge the battery up twice as quickly and use much less fuel. 20A x 14V is now a more respectable 280W load on your 2kW generator.
If you have multiple batteries, get an even bigger charger. i.e a 40A charger for 2 x 100Ah batteries.
If you have a solar controller that does not output battery voltage, instantaneous charge, and accumulated charge, invest $15 or so on buying one of these on eBay. Note that these will only measure current on ONE direction. So they are good for measuring solar panel output but not good for measuring charge into and discharge out of a battery.
cheers