An amp meter in one of the solar feeds, before connecting up the second one could confirm the flow is reversing because it has to be going somewhere
So did some testing today, bit overcast and afternoon so no steady current but enough to get some results (they just won't match directly between tests). Roof panel was partly shaded hence the low amps.
With TPS controller fully disconnected from all panels (+ and -): Roof Voc 20.0V, Isc 0.9A Portable Voc: 22.8V, Isc 11.8A Combined Voc 21.8V, Isc 13.85A Combined, with one of the two portable panels fully covered Voc 21.0V, Isc 6.24A
With TPS controller connected to each individual panel, similar results re current
With TPS controller connected to both portable and roof in parallel, briefly showed 8.0A on screen and meter then went to zero on both. Disconnecting and connecting in any combo could not repeat this, always went to zero amps after this when panels in parallel. Putting meter in series to portable showed -1.6A, meter in series with roof showed 6.2A.
Maybe it's just the TPS (PWM) doing what it's supposed to since all these tests were done when the batteries were pretty much full. I'll try and do a test where the panels are connected in parallel and I turn on a bunch of stuff (including the inverter with load) to force the TPS into Constant Power mode (ie full current from solar to batteries) and see if it pops up above zero.
Good point Mike. I missed that bitThe fact that one panel was showing -ve current is an indication that you need blocking diodes in series with each panel.
The fact that one panel was showing -ve current is an indication that you need blocking diodes in series with each panel.
If you look inside the terminal box on each panel, are there any diodes in there?
If so, can you post photos of the terminal boxes. Thet will probably be wired as bypass diodes but you may be able to rewire them as bypass diodes.
cheers
Mike
Hi.@mikerezny , normally the controllers have their own blocking diodes, thus preventing power loss from battery at night. I am sure the TPS would have this integrated into its circuit. It would appear that used individually through the TPS, there is no problem, but there appears to have a "bleed" back through the portable panel when both connected. That means there is higher resistance through TPS to battery than through the portable which should not conduct anyway. Causing a short circuit back to battery?? Interesting. I also want to see pictures of connections/diodes in junction box.
Hi.
A solar controller does indeed prevent the battery from discharging into a panel when there is no sun. But, when panels are wired in parallel, it does not prevent one panel in the sun from discharging into a panel that is not in the sun. Hence the need for blocking diodes.
This has been discussed in detail in previous posts. Otherwise do a Google on Blocking and Bypass diodes. Basically, bypass diodes in parallel across panels wired in series and blocking diodes in series with panels wired in parallel.
Ideally, all panels in parallel should have the same Voc.
cheers
Mike
So the panels in parallel are showing the expected VOC if i'm reading your post correctly so the wiring is ok.
I don't know if it is smart enough, but it could be starting and seeing too much current flow and disconnecting, or starting and seeing a sudden rise in battery voltage (over 14.7 from memory) and disconnecting. The TPS pulses the panel current into the batteries - a longer pulse gives higher current - until the battery voltage starts to rise, and then it shortens the pulses as the battery reaches 14.7. (You probably know this but thats where the PWM term comes from - Pulse Width Modulation). So it may try an initial pulse (the 8amps you mention), measure the battery voltage, and decide to stop further pulses/ charging.
Leaving it all hooked up and turning on a few lights to get the load up to 10 amps might test this. I would expect the TPS to start up to try and maintain 14.7V.
Hi,With TPS controller fully disconnected from all panels (+ and -): Roof Voc 20.0V, Isc 0.9A Portable Voc: 22.8V, Isc 11.8A Combined Voc 21.8V, Isc 13.85A Combined, with one of the two portable panels fully covered Voc 21.0V, Isc 6.24A
Hi @Boots in Action ,
Oops, my bad. Couldn't read 30A on one page and write it in a post without making a mistake. Agree, it is 30A maximum for the TPS1230. I have edited the that post to correct the mistake.
Still, something weird going on with these two panels. Need to do some faultfinding, and, I would suggest, the first step would be to put a blocking diode in series with each panel to eliminate this as the cause of the problem.
cheers
Mike
Zero voltage is an indication of open circuit or short circuit in my opinion
I would try another controller firstly and confirm that the problem still existed. Saves soldering. Then if condition still exists and connections are correct at panel, then purchase diodes and fit for testing further. Cheers and keep up the good work. Also see my latest post to @jazzeddie1234 .